System Design exceeds Inverter Maximum DC current: No Error Message was created by Patrick
Hello Paul,
I have a the following components:
My SAM simulation file is attached.
Best,
Patrick
I have a the following components:
- PV Module: Short circuit current (Isc) = 9.81 A
- Inverter: Maximum DC current = 49.5 Adc
- Number of inverters = 20
- Strings in parallel in subarray = 120
- Total PV: 9.81 A * 120 = 1177 A
- Total Inverter: 49.5 Adc * 20 = 990 Adc
- Results: 990 Adc < 1177 A
My SAM simulation file is attached.
Best,
Patrick
Last edit: 30 Nov 2021 11:22 by Patrick. Reason: Input mistake in the attached SAM file: The Systen Design uses only one MPPT input but the inverter had two MPPT inputs defined, which results in an error in the simulation. Therefore, the new file.
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5760
29 Nov 2021 18:09 #10323
by Paul Gilman
Replied by Paul Gilman on topic System Design exceeds Inverter Maximum DC current: No Error Message
Hi Patrick,
During the simulation, SAM limits the inverter input voltage to the min and max MPPT voltage ratings and its AC output power to the rated AC output power, but does not check the input current.
You can check the short circuit current of each subarray in the outputs to see if it exceeds the rated limit. For example, on the Statistics tab of the Results page after running a simulation, look at the "Max" value of Subarray 1 String short circuit DC current (A).
Best regards,
Paul.
During the simulation, SAM limits the inverter input voltage to the min and max MPPT voltage ratings and its AC output power to the rated AC output power, but does not check the input current.
You can check the short circuit current of each subarray in the outputs to see if it exceeds the rated limit. For example, on the Statistics tab of the Results page after running a simulation, look at the "Max" value of Subarray 1 String short circuit DC current (A).
Best regards,
Paul.
Please Log in or Create an account to join the conversation.
- Patrick
- Topic Author
Less
More
- Posts: 4
30 Nov 2021 11:33 #10329
by Patrick
Replied by Patrick on topic System Design exceeds Inverter Maximum DC current: No Error Message
Thanks, Paul!
I followed your instruction and Subarray 1 String short circuit DC current (A) = 10.8 A
How is this possible when one module hence one string has a Short circuit current (Isc) = 9.81 A ? I assumed that the Subarray 1 String short circuit DC current (A)should never exceeds 9.81 A, but it does?
In my System Design with 120 strings in parallel, this would result in 120 * 10.8 A = 1296 A. This is significantly more than the 20x inverter's max. DC input current of 49.5 Adc per inverter, meaning 20 * 49.5 Adc = 990 Adc < 1296 A. Wouldn't be a warning by SAM useful?
Thank you again for your time! Best, Patrick
I followed your instruction and Subarray 1 String short circuit DC current (A) = 10.8 A
How is this possible when one module hence one string has a Short circuit current (Isc) = 9.81 A ? I assumed that the Subarray 1 String short circuit DC current (A)should never exceeds 9.81 A, but it does?
In my System Design with 120 strings in parallel, this would result in 120 * 10.8 A = 1296 A. This is significantly more than the 20x inverter's max. DC input current of 49.5 Adc per inverter, meaning 20 * 49.5 Adc = 990 Adc < 1296 A. Wouldn't be a warning by SAM useful?
Thank you again for your time! Best, Patrick
Please Log in or Create an account to join the conversation.
- Paul Gilman
Less
More
- Posts: 5760
08 Dec 2021 16:37 #10368
by Paul Gilman
Replied by Paul Gilman on topic System Design exceeds Inverter Maximum DC current: No Error Message